Problem 4: Heat Exchangers Analysis (25 points) A counterflow plate-type heat exchanger as shown in the figure below is used
0 0
Add a comment Improve this question Transcribed image text
Answer #1

Fic Teh6 Tin fropene 0340 water balance quaron wat Heal fo b gain by Cooingfloid h TTne)-m Te-Te) Hot Heat Pluid 0.2xp178 (Te25. oB C Tee LMTD For onter low LMTD 40 MTD 60-40 2o MTD (am) 20 49,32 Om 49. 826 c UAOM hw l0G.82 hp 1esk 6G.103 m2 K2 20.0/small Oomee= ) Co10) man COmon 6S X0.1XI70 OSol C0UAOM /1osO A 64.103x 49326 3.494Cm2 A Reetamguter duet tpe Areg of Heat ex3.4946 o.IS lonyth lemgth 3. 2973 m ength of heat Cc hanger yegi red to condensed propame Cxc 93.2973 m

Add a comment
Know the answer?
Add Answer to:
Problem 4: Heat Exchangers Analysis (25 points) A counterflow plate-type heat exchanger as shown in the...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Problem X3-5, Heat Transfer, Spring 2018 A single-pass, double-tube counterflow heat exchanger will be used to...

    Problem X3-5, Heat Transfer, Spring 2018 A single-pass, double-tube counterflow heat exchanger will be used to heat a 0.14 kg/s stream of water nowing in the 12-mm diameter inside tube. The water in the inside tube enters the heat exchanger at 25 C. The water will be heated with a 0.12 kg/s m of hot water flowing in the annulus between the inside and outside tube that enters the heat exchanger at 80°C. UP the hot and cold streams, and...

  • The condenser of a large steam power plant is a heat exchanger in which steam is...

    The condenser of a large steam power plant is a heat exchanger in which steam is condensed to liquid water. Assume the condenser to be a shell-and-tube heat exchanger consisting of a single shell and 30,000 tubes, each executing two passes (see figure below). The tubes are of thin wall construction with D=25mm, and steam condenses on their outer surface with an associated convection coefficient ho=11,000W/ m K The heat transfer rate that must be effected by the heat exchanger...

  • heat transfer Test Yourself A Shell-and-tube heat exchanger, consisting of a single shell and 30.000 tubes,...

    heat transfer Test Yourself A Shell-and-tube heat exchanger, consisting of a single shell and 30.000 tubes, each executing two passes, is used in a large steam power plant to condense steam to liquid water. The steam condensed in the shell side of the heat exchanger with an associated convection coefficient (h) of 11.000 W/m2.°C. The heat transfer rate through the heat exchanger (O is 2x10' W. Cooling water is passing through a thin tubes with D = 2.5 cm, at...

  • Problem (25 Points - Chapter 11) A concentre tube heat exchanger for cooling lubricating oil is...

    Problem (25 Points - Chapter 11) A concentre tube heat exchanger for cooling lubricating oil is comprised of a thin-walled me tube of 25-mm diameter carrying water and an our tube of 45mm diameter coming the The heat exchanger operates in counterflow with an overall heat transfer coefficient of W K and the average property as given in the table below. If the outlet temperature of the oil is 60°C, determine the following (a) total heat transfer rate, (b) outlet...

  • A concentric tube heat exchanger for cooling lubricating oil consists of a thin-walled inner tube of...

    A concentric tube heat exchanger for cooling lubricating oil consists of a thin-walled inner tube of 25 mm diameter carrying water and an outer tube of 45 mm diameter carrying the oil. The exchanger operates in countercurrent flow with an overall heat transfer coefficient of 55 W/m2 K and the tabulated average properties given below. Mass flow rates of oil and water are both 0.1 kg/s, oil enters the exchanger at 100°C, and water enters the exchanger at 30°C. (a)...

  • A counter-flow heat exchanger is stated to have an overall heat transfer coefficient of 284 W/m2.K...

    A counter-flow heat exchanger is stated to have an overall heat transfer coefficient of 284 W/m2.K when operating at design and clean conditions. Hot fluid enters the tube side at 101°C and exits at 71°C, while cold fluid enters the shell side at 27°C and exits at 42°C. After a period of use, built-up scale in the heat exchanger gives a fouling factor of 0.0004 m2 K/W. The surface area is 93 m². Assume both hot and cold fluids have...

  • PROBLEM 3 (45 points) The condenser of a large steam power plant is a heat exchanger...

    PROBLEM 3 (45 points) The condenser of a large steam power plant is a heat exchanger in which steam is condensed to liquid water. Assume the condenser to be a parallel flow shell-and-tube heat exchanger consisting of a single shell and 1x10 tubes, each executing two passes. The inner diameter of tubes is D = 50 mm and its thickness is 5 mm (Do not ignore the thickness). The steam condenses on their outer surface. Thermal conductivity of the tube...

  • Problem 2: Heat exchanger (25 points) Cold water (op 4179 J/kg K) enters the tubes of a heat exchanger at 20 °C at a rate of 3 kgs. while hot oil (cp 2200 J/kg.K) enters the shell at 130 C at the sam...

    Problem 2: Heat exchanger (25 points) Cold water (op 4179 J/kg K) enters the tubes of a heat exchanger at 20 °C at a rate of 3 kgs. while hot oil (cp 2200 J/kg.K) enters the shell at 130 C at the same mass flow rate and leaves at 60°C The heat exchanger consistsoftwo shells and 20 tubes, each executing four passes (two passes per shell). If the W/m2-K, assume the tube wall is very thin with convective heat transfer...

  • Problem 3. (25 points) In a Rankine power system, 1.5 kg/s of steam leaves the turbine...

    Problem 3. (25 points) In a Rankine power system, 1.5 kg/s of steam leaves the turbine as saturated vapor at 0.51 bar. The steam is condensed to saturated liquid by passing it over the tubes of a shell-and-tube heat exchanger, while liquid water, having an inlet temperature of T = 280 K, is passed through the tubes. The condenser contains 100 thin-walled tubes, each of 10-mm diameter, and the total water flow rate through the tubes is 15 kg/s. The...

  • 25 PRR HEAT TRANSFER NAME: UNIT SIX AND SEVEN EXCHANGERS BOILING AND CONDENSATION, He- Solve the following problems:...

    25 PRR HEAT TRANSFER NAME: UNIT SIX AND SEVEN EXCHANGERS BOILING AND CONDENSATION, He- Solve the following problems: 1. In a gas-faired boiler, water is boiler at 150 C by hot gases flowing through 59 m long, 5 cm outer diameter mechanically polished stailess-stell pipes submerged in water, If the outer surface temperature of the pipes is 180 °C. determine (a) the rate of heat transfer from the hot gases to water. (b) the rate of evaporation, (c) the ratio...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT