Q3. (a) A star-connected, 3-phase, 10-MVA, 6·6 kV alternator has a per phase reactance of 10%. It is protected by Merz-Price circulating-current principle which is set to operate for fault currents not less than 175 A. Calculate the value of earthing resistance to be provided in order to ensure that only 10% of the alternator winding remains unprotected.
Q3. (a) A star-connected, 3-phase, 10-MVA, 6·6 kV alternator has a per phase reactance of 10%....
A 36 MVA, 20.8 kV, 3-phase alternator has a synchronous reactance of 9 Q and a nominal current of 1 kA. The no-load saturation curve giving the relationship between Eo and I, is given in Fig. 13b. If the excitation is adjusted so that the terminal voltage remains fixed at 12 kV, calculate the exciting current required and draw the phasor diagram for the following conditions: No-load а. b. Resistive load or 36 MW Capacitive load of 12 Mvar C....
QUESTION 5 A 3-phase, 22 kV (phase), 500 MVA star-connected synchronous generator has a per phase reactance Xg of 1.5 pu and supplies 0.8 pu per phase real power (P) at the rated voltage, with a lagging power factor of 0.6 to the load. Find the actual excitation voltage Vo in kV (line value). 96.392
Question I The rating of a three phase three winding transformer are: Y-connected 10 KV 40 MVA Secondary Y-connected 22 KV 40 MVA A-connected 4 KV 15 MVA Primary Tertiary Neglecting winding resistance and exciting current, the per unit leakage reactance are: Mps 9.6 % pu on 40 MVA, 11022 KV xm = 7.2 % pu on 40 MVA, I 10/ 4 KV Xsti: 12 % pu on 40 MVA, 22/ 4 KV Determine the era nyimpedances of the transformer...
3 A 11-KV, has a full-load quadrature-axil IV. three-phase, 20-pole, star-connected, salient-pole synchronous alternator full-load current of 1000 A The resistance of the rotor is 1,2 phase The rature-axis synchronous reactance per phase is 4.8 and the direct-axis nchronous reactance per phase is 3, 62 Determine for a lagging power factor of 0,8 a) the load angle, b) the developed power, c) the reluctance torque, and d) the voltage regulation СНАР 245 MM401EE
A 13.8 kV, 10 MVA, 0.8 pf lagging, 60 Hz two-pole star-connected steam-turbine generator has a synchronous reactance of 12 Ω per phase and an armature resistance of 1.5 Ω per phase. This generator is operating in parallel with a large power system (infinite bus). At the absolute maximum power possible, how much reactive power will this generator be supplying or consuming? Sketch the corresponding phasor diagram. (Assume IF is still unchanged.)
A 208 V, star-connected, 3-phase synchronous motor has a synchronous reactance of 4 ohms/phase and negligible armature winding resistance. At a certain load, the motor takes 7.2 kW at 0.8 pf lagging. If the power developed by the motor remains the same while the excitation voltage is increased by 50% by raising the field excitation, determine (a) the new armature current and (b) the new power factor.
A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.5Q/phase and a synchronous reactance of 5Q/phase. The generator is supplying its rated power at its rated voltage and at a power factor lagging. The rotational loss is 2 kW. Calculate: (a) the power developed, (b) the power angle, (c) the voltage regulation, and (d) the shaft torque. A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.50/phase and a synchronous...
3. A 722-MVA, 19-kV steam turbine generator has a per-phase synchronous reactance of 1.3 PU, and its internal (excitation) voltage is adjusted to 1.2 PU. The generator is connected to a 19 kV (line) infinite-bus. If the voltage angle (d) between the infinite-bus and the generator internal voltage is 20°, calculate, The generator active power output. The generator line current. Draw the phasor diagram for one phase.
1- A 25-kVA, 3-phase, wye-connected, 400-V alternator has a synchronous reactance of 1.6 ohms per phase. The alternator is to have zero voltage regulation at half-load. Neglecting the armature resistance, find the operating power factor and the developed power 2. A 500-kVA, 3600-V, 3-phase, 60-Hz alternator has an effective armature resistance per phase of 0.40 ohm Mechanical and iron losses is 10 kW, field current at full load unity power factor is 70 A. The exciter voltage is constant at...
A 3-phase transformer 50 MVA, having line-voltage ratio of 11 kV/33kV is connected in star-delta What must be the ratio of the protective transformers on the both sides?