Question

You work as an engineer in the control department of a transformer manufacturer. A transformer with...

You work as an engineer in the control department of a transformer manufacturer. A transformer with
the following nameplate data is manufactured after long 6 months. For the final delivery, you need to
determine the electrical resistances and electrical reactances. Nameplate data: A single phase, 150MVA,
300/100kV transformer.
(a) What type of tests you would apply to the transformer to calculate such data?
(b) Short-circuit test results are: 40 kV, 600 kW losses. Which two data you can calculate from this
test, then calculate them.
(c) Open-circuit test results are: 24 A, 12kW power losses. Which two data you can calculate from
this test, then calculate them.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Name plate details : 150 mUA. 300/100 KUA. ca). To calculate the electrical senstance and reactances of the transformer we ca↑ Isc Roi Xol ib) SC Tests Vsc = 40 KV Wsc = 600kW, loc u Isc = VA rating HV Volterge = 150X10 300x103 = 500A Zona eve you toSindo i sin (89.91) = 0,9999 Roz Va To,cos do looxio² 24 X 00005 = 833.33 km Voc xon 100x10 24x0.9999 .. locsindo = 4170.84.2

Add a comment
Know the answer?
Add Answer to:
You work as an engineer in the control department of a transformer manufacturer. A transformer with...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 1200 kVA, 11/3.3 kV, 50-Hz, three phase Dyn 11 transformer is subjected to both the...

    A 1200 kVA, 11/3.3 kV, 50-Hz, three phase Dyn 11 transformer is subjected to both the open, and short circuit tests, yielding the following results: OPEN CIRCUIT TEST SHORT CIRCUIT TEST Vsupply = 3.3 kV Vsupply = 650 V Io = 7.3 A Isc = 54.4A Po = 6.71 kW Psc = 8.89 kW Determine: 1.1 The no load current per phase, in RECTANGULAR form, referred to the H.V. side. (5) 1.2 How would you know, without being told, that...

  • A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio...

    A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio 15:0.4 kV. After conducting the short-circuit test, where the secondary winding is short-circuited, it is found that the primary series resistance is 0.08 pu and the primary series impedance magnitude is 0.1pu. The effect of the parallel branch in the transformer’s equivalent circuit may be neglected. Explain what information ‘Yy0’ gives about the transformer. Draw the per-phase equivalent circuit of the transformer during the...

  • solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power...

    solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power System Analysis 3.12. A single-phase system similar to that shown in Figure 3.11 has two transformers A-B a B-C connected by a line B feeding a load at the receiving end C. The ratings and parame ter values of the components are 500 V/1.5 kV, 9.6 kVA. leakage reactance 5 % 1.2 kV/120 V, 7.2 kVA, leakage reactance 4 % series impedance (0.5 +...

  • can you calculate this question and explain why? thanks 1. A 250-kVA, 11000/2200-V, 50-Hz, single-phase transformer...

    can you calculate this question and explain why? thanks 1. A 250-kVA, 11000/2200-V, 50-Hz, single-phase transformer has the following parameters: RI 1.3 , R2 0.05 , Rel 193 k2, X1 4.5 Q X2 0.16 2 I,- 80 kQ Xml (a) Draw the approximate equivalent circuit of the transformer showing all the circuit parameters referred to the low-voltage side. Use the approximate equivalent circuit to calculate the input voltage and voltage regulation of the transformer when it delivers full load at...

  • Can you help me with this situation and explain the questions? Suppose an engineer designs a...

    Can you help me with this situation and explain the questions? Suppose an engineer designs a 120/240 Volt single phase power system for a restaurant including the indoor wiring circuits. He had some conversations with the restaurant owner prior to completing his final design but the owner was not very organized so only shared the other kitchen equipment technical specs by telephone. The restaurant hired an electrician to install the kitchen equipment and inside wiring. However, when the owner met...

  • An electrical engineer must design a circuit to deliver the maximum amount of current to a...

    An electrical engineer must design a circuit to deliver the maximum amount of current to a display tube to achieve sufficient image brightness. Within her allowable design constraints, she has developed two candidate circuits and test prototypes of each. The resulting data (in microamperes) are as follows: Test for evidence that the first circuit can deliver a higher current that circuit 2 using a 5% level. You may assume that the populations are normal for this problem. Show all work...

  • UNIT TEST 1. Which of the following statements is a characteristic of a control transformer? a....

    UNIT TEST 1. Which of the following statements is a characteristic of a control transformer? a. b. Permits switching off the load Prevents motor overload c. d. Provides control voltage compatible with relay coils Enables motor phase reversal 2. Which contactor utilization category permits plugging operation? a. AC-1 b. AC-2 с, АС-3 d. AC-4 3. What happens as power returns, in a three-wire motor circuit, following a pow failure? a. The motor restarts automatically b. The motor remains de-energized. c....

  • [29] SECTION B: TRANSFORMERS QUESTION 2 2.1 A 240:48-volt, 50-F power factor of 0.8 lagging. If...

    [29] SECTION B: TRANSFORMERS QUESTION 2 2.1 A 240:48-volt, 50-F power factor of 0.8 lagging. If the no load current and iron loss of this e transformer supplies a load of 10 ampere at a ampere and 12-watt respectively, calculate the total current supplied and the powe oad current and iron loss of this transformer are factor. (7) KVA, 50-Hz, 1200:230-volt single phase transformer has the following series impedance values: Z1 = (0.047 +0.112) Z2 = (0.00172 +0.00411)2 Calculate: 2.2.1...

  • (17 Points) An electrical engineer must design a circuit to deliver the maximum amount of current...

    (17 Points) An electrical engineer must design a circuit to deliver the maximum amount of current to a display tube to achieve sufficient image brightness. Within her allowable design constraints, she has developed two candidate circuits and test prototypes of each. The resulting data (in microamperes) are as follows: Circuit 1: 251 255 258 257 250 251 254 250 248 Circuit 2: 250 253 249 256 252 260 251 259 Test for evidence that first circuit can deliver a higher...

  • A manufacturer of home products is designing a new wall mount for large flat-panel televisions. Since...

    A manufacturer of home products is designing a new wall mount for large flat-panel televisions. Since some flat-panel televisions weigh up to 100 pounds, the manufacturer wants to make sure that the mean weight of failure for the wall mounts is greater than 180 pounds. Dayton is a researcher for the manufacturer who is conducting the test. He randomly selects 35 wall mounts and tests them by using a machine that pulls down on the mounts until each one fails....

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
Active Questions
ADVERTISEMENT