Question

Please do study question 4.18 4.18: For the transformer of Problem 4.15, draw approximate equivalent circuits...

Please do study question 4.18

4.18: For the transformer of Problem 4.15, draw approximate equivalent circuits
as viewed from (a) the primary side and (b) the secondary side. In each
case, determine (a) the efficiency and (b) the regulation if the load has a
lagging power factor of 0.8.

4.15: A 230-kVA, 2300/230-V, 60-Hz, step-down, two-winding transformer has
the following parameters R(H), = 1.2 ohms, X(H), = 3ohms, R(L), = 12 mohms, X(L) , = 30 mohms,
R(CH), = 2 kohms, X(MH), = 1.8 kohms. If the transformer operates at half load at its
rated terminal voltage with a unity power factor, what is its efficiency?

0 0
Add a comment Improve this question Transcribed image text
Know the answer?
Add Answer to:
Please do study question 4.18 4.18: For the transformer of Problem 4.15, draw approximate equivalent circuits...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 2.14 The resistances and leakage reactances of a 40-kVA 60-Hz 7.97-kV-V:240-V single-phase distribution transformer are where...

    2.14 The resistances and leakage reactances of a 40-kVA 60-Hz 7.97-kV-V:240-V single-phase distribution transformer are where subscript 1 denotes the 7.97-kV winding and subscript 2 denotes the 240-V winding. Each quantity is referred to its own side of the transformer. Consider a rated-kVA load connected at the low-voltage terminals. Assuming the load voltage to remain constant at 240 V use MATLAB to plot the high-side terminal voltage as a function of the power-factor angle as the load power factor varies...

  • Electric Machinery Problem 2: [50 points] A 15-KVA, 230/2300-V transformer is considered. The following test data...

    Electric Machinery Problem 2: [50 points] A 15-KVA, 230/2300-V transformer is considered. The following test data have been taken: | OC Test (on Primary) Voc = 230 V loc = 2.8 A Poc = 100 W SC Test (on Secondary) Vsc = 47 V Isc = 9.5 A Psc = 350 W (a) Find the equivalent circuit of this transformer referred to the high- voltage side. [10 points] (b) Find the equivalent circuit of this transformer referred to the low-...

  • Q-1 A 60Hz, 480V/240V,960V A transformer is supplying a 960W passive load at 240V. The resistances...

    Q-1 A 60Hz, 480V/240V,960V A transformer is supplying a 960W passive load at 240V. The resistances of the primary side and secondary side of the transformer are 1.092 and 0.252 respectively. If the no load losses of the transfomer is given by P-Vã 4800 W where Vn is the input voltage of the transformer in Volt. Answer the following: a) Calculate transformer efficiency b) Do you allow this transformer to be connected to 240V 50Hz distribution system? Explain. c What...

  • (a) Describe the tests carried out on a single-phase transformer to determine its equivalent circuit parameters...

    (a) Describe the tests carried out on a single-phase transformer to determine its equivalent circuit parameters and explain how each parameter is determined based on the test results. (b) A 2200/220 V, 15 kVA, single phase transformer has the following equivalent circuit parameters: The HV winding resistance and leakage reactance are 0.2Ω and 0.3Ω respectively. The LV winding resistance and leakage reactance are 0.012Ω and 0.03 Ω respectively. The magnetic circuit resistance and reactance referred to the HV side are...

  • A 150 KVA, 2080/208-V, 3 PHASE, delta-wye transformer with the following: RH 450m2 R 4.5m XH 2.20...

    A 150 KVA, 2080/208-V, 3 PHASE, delta-wye transformer with the following: RH 450m2 R 4.5m XH 2.20 Load 120 KVA, 90KW (lagging power factor) at rated terminal voltage of 208V Determine a) b) c) The approximate equivalent circuit referred to the low-voltage side The primary voltage The transformer efficiency Please show the following: Circuit with the values given & found Equations used A 150 KVA, 2080/208-V, 3 PHASE, delta-wye transformer with the following: RH 450m2 R 4.5m XH 2.20 Load...

  • Q1 A single-phase 11/2.2 kV, 22 kVA transformer has the following parameters all referred to the HV side RI 0.4, X 0...

    Q1 A single-phase 11/2.2 kV, 22 kVA transformer has the following parameters all referred to the HV side RI 0.4, X 0.602, R2 7.5 , X2 22 , Re 2500 , and Xm - 20002 The transformer is supplying 80% of its rated load at a power factor of 0.87 power factor lagging and at its rated voltage. Calculate (a) the efficiency of the transformer, (b) the power losses on the primary side (the copper loss and core loss), and...

  • Problem 1: A three-phase transformer has the following name plate data: Rated Power Primary voltage Secondary...

    Problem 1: A three-phase transformer has the following name plate data: Rated Power Primary voltage Secondary Voltage Excitation reactance Series Impedance 150 MVA 230 kV 32 kV 30 (pu) 0.02+0.15j (pu) The transformer is Y/A connected. Answer the following questions: a) What are the nominal (rated) primary and secondary line currents?| b) What is the nominal value of the Delta-side winding (internal) current? c) What is the secondary to primary winding turn ratio? d) The transformer is supplying 150 MVA...

  • A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting thre...

    A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting three single phase transformers in the Dynll vector group as shown in Fig.P1. The per phase equivalent circuit parameters on the high voltage side are: R1-0.72 Ω, Xi,-0.92 Ω, R2-0.70 Ω, Xp-0.90 Ω, R.-308.49 Ω, and X,,-44.61 Ω (a) Sketch the corresponding phasor diagram of the primary and secondary voltages for the Dynll vector group; lagging; terminal voltage is 415 V line to line, and...

  • Problem (1): A 15-KVA, 2400:240-V, 60 Hz transformer has the following equivalent circuit parameters: R =...

    Problem (1): A 15-KVA, 2400:240-V, 60 Hz transformer has the following equivalent circuit parameters: R = 2.522 R2 = 0.02522 Xi = 722 X = 0.0712 Re = 32 kl Xm = 11.5 k12 If the transformer is supplying a 10-kW, 0.8 PF lagging load at rated voltage, assuming the output voltage is the reference, draw the transformer's exact equivalent circuit referred to the primary (H.V) side and use it to calculate: 1. The input current 2. The input voltage...

  • Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60...

    Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60 Hz. The following results are obtained from open-circuit and short-circuit tests: Test Open-circuit Short-circuit Voltage 7200 V 250 V Current 0.65 A 13.89 A Real Power Input 425 W 1420 W a) Determine the parameters of this transformer, all referred to the primary side. b) The secondary of this transformer is connected to a load that draws 100% of the rated power at rated...